Power Systems MCQs

Power systems, the way the papers ask it — generation from hydro, thermal, nuclear and renewables, transmission at high voltage with its corona, skin effect and Ferranti effect, distribution through substations and feeders, transformers and their protection, relays, circuit breakers, fuses and earthing, load factor, diversity factor and tariffs, and Pakistan's own power sector: WAPDA, NTDC, the DISCOs and the great dams, from Tarbela's 4,888 MW to the 4,000 MW HVDC line.

Facts checked 28 November 2026.131 practice MCQs on this topic

Power Systems — Study Notes

What to learn in Power Systems

This topic is power systems the way the one-paper exams ask it: the whole journey of electricity from the place it is made to the place it is used, and the numbers, the equipment and the rules that govern each step of that journey. There are 131 practice questions on this page: 104 from the bank and 27 new ones written to fill the gaps the bank leaves — most of them where the bank has a definition but never the working: the diversity factor and the demand factor as numbers, the capacity factor of a plant, the two-part tariff, the area under a load curve, a hydroelectric power calculation, the isolator that must never be opened on load, the tap changer and the cooling of a transformer, the sag of a line and the voltage across a string of insulators, and the Pakistan facts the bank only half covers — Mangla, Ghazi Barotha, Diamer-Basha, the first nuclear plant at Karachi and the solar park at Bahawalpur. The order below is the order to learn in. Start with the system in one picture, because every later section is one box in that picture: generation, transmission, distribution and the consumer. Then generation — hydro, thermal, nuclear and the renewables — and the one formula the papers ask, the hydroelectric power formula. Then transmission, where the high voltage, the conductors, corona, the skin effect and the Ferranti effect live. Then distribution — the radial and ring systems, the substation, the feeder and the cables. Then the transformers and the protection that guard the system: relays, circuit breakers, fuses, earthing and lightning arresters. Then the load and the money: load factor, diversity factor, tariffs and the load-flow study. Last, Pakistan's own power sector — WAPDA, the national grid, the distribution companies and the big dams and plants. Past papers — BPSC, CTS, NTS, PPSC and FPSC assistant-engineer, sub-divisional-officer and assistant-lineman papers — ask the same core facts again and again: why high voltage, what a step-up transformer does, what a circuit breaker does, what load shedding is, what WAPDA stands for, which dam is the largest hydroelectric station in Pakistan. Learn each fact with its number and its reason, and each of those questions becomes a recognition, not a guess. Two boundary rules for this page. First, pure circuit theory stays in Circuit Theory: Ohm's law, Kirchhoff's laws, the network theorems, the power triangle and the star-delta voltage relations are taught there, and the questions that only test those definitions have been moved out — this page uses power factor and reactive power, but it does not re-teach their definitions. Second, transformers, motors and generators as machines belong to Electrical Machines: this page covers transformers only where they serve the system — stepping voltage up at the station and down at the substation, and the Buchholz and differential protection that guard them — and it covers generators only as the source of the power, at the voltage they generate. One honest note on scope: the exact installed capacities of Pakistan's plants change as extensions are commissioned — Tarbela grew from 3,478 MW to 4,888 MW with its fourth extension — so learn the ranking and the order of size, not only the number, and treat the capacities in the notes as the figures current when this page was written.

I. The power system in one picture

A power system has four parts, and every question on this page is about one of them. Generation makes the electricity, in a power station. Transmission carries it over long distances, at high voltage, on overhead lines held up by steel towers. Distribution delivers it to towns and streets, stepping the voltage down in substations until it reaches homes. The load is everything that uses the power — the equipment that uses electrical power, from a bulb to a factory motor. The voltage changes at every step, and the papers test the whole ladder. Electricity is typically generated at 11 kV in a power station — modern generators produce roughly 13 kV to 30 kV at their terminals. A step-up transformer at the station raises it for transmission: Pakistan's main high-voltage transmission network runs at 500 kV, and 400 kV and above is the level typically used for long-distance transmission. Grid stations step it down to 132 kV, primary distribution runs at 11 kV, and a distribution transformer lowers it again for supply to homes — the domestic supply in Pakistan is single-phase 230 V at 50 Hz, with three-phase supply at 400 V. The frequency is the same everywhere in the system: Pakistan's supply is 50 Hz, while the United States uses 60 Hz. One unit of electricity on a bill is one kilowatt-hour, and an energy meter measures the amount of electricity used. The load is not steady: when demand is greater than supply, the system operator cuts supply in a planned way, and that planned cut is load shedding — the planned disconnection of supply when demand exceeds generation. A feeder carries electricity from a substation to the consumers, and a substation itself is the place where voltage levels are changed and power is distributed: it houses the transformers, the busbars and the switchgear. A busbar is the conductor in a substation that collects power and distributes it to the outgoing feeders.

The voltage ladder in Pakistan
  • Generation — typically 11 kV at the power station; modern generators produce about 13 kV to 30 kV.
  • Main transmission — 500 kV; long-distance transmission uses 400 kV and above.
  • Grid stations — stepped down to 132 kV.
  • Primary distribution — 11 kV.
  • Homes — single-phase 230 V at 50 Hz; three-phase supply 400 V.
The four parts, one line each
  • Generation — a power station generates electrical power; a generator produces electricity.
  • Transmission — a transmission line carries power from the power station to where it is used.
  • Distribution — substations and feeders deliver power to consumers.
  • Load — the equipment that uses electrical power.

II. Generation: hydro, thermal, nuclear and renewables

Every power station is an energy conversion, and the papers ask what is converted into what. A thermal power plant converts heat into mechanical energy and then into electrical energy: fuel is burned, steam drives a turbine, and the turbine drives the generator. Its efficiency is set above all by the temperature difference between the heat source and the sink — the hotter the source and the colder the sink, the more of the heat can become work. A 500 MW thermal plant running at 38% efficiency needs about 1,316 MW of heat input, which is why the coal it burns each hour is measured in hundreds of tonnes. Inside the plant, each part has one job: the economizer preheats the feedwater using the residual heat of the flue gases, so heat that would leave through the chimney is used first. A hydroelectric power station converts the energy of falling water: its power output is set by the height of the water head and the flow rate, and the formula is P = ρgQHη, where ρ is the density of water (1,000 kg/m³), g is 9.81 m/s², Q is the flow rate and H is the effective head, multiplied by the overall efficiency η. A flow of 500 cubic metres per second falling 120 metres at 85% efficiency gives about 500 MW. A nuclear power plant works the same way as a thermal plant once the heat exists, but the heat comes from fission, and the moderator is the part that slows down fast neutrons so the chain reaction can be sustained. Renewables need no fuel at all: hydro, solar and wind are the three the papers name, and the smart grid exists largely to take them in, because their output changes with the weather. The generation voltage matters too: a generator does not produce 500 kV directly — it produces about 11 kV to 30 kV, and the step-up transformer does the rest.

The energy conversions
  • Thermal plant — heat to mechanical energy to electrical energy.
  • Hydroelectric plant — falling water to mechanical energy to electrical energy; power depends on head and flow rate, P = ρgQHη.
  • Nuclear plant — fission heat to steam to mechanical energy to electrical energy; the moderator slows fast neutrons to sustain the chain reaction.
  • Renewables — hydro, solar and wind need no fuel; their output varies with the weather.
Pakistan's hydroelectric stations
  • Tarbela Dam, on the Indus — Pakistan's largest hydroelectric power station, 4,888 MW after its fourth extension, and the largest earth-filled dam in the world.
  • Mangla Dam, on the Jhelum — 1,000 MW.
  • Ghazi Barotha, on the Indus — 1,450 MW, the country's second largest hydroelectric station.
  • Warsak Dam, on the Kabul — 243 MW, completed in 1960, the country's first major hydroelectric project.
  • Diamer-Basha Dam, on the Indus — 4,500 MW, under construction.
  • Dasu, on the Indus — 2,160 MW in its first phase, under construction.
Pakistan's other generation
  • KANUPP, at Karachi — Pakistan's first nuclear power plant, commissioned in 1972.
  • Chashma Nuclear Power Plant, at Chashma in Mianwali — built with China's cooperation; the Chashma-5 agreement was signed with China in 2023.
  • Quaid-e-Azam Solar Park, at Bahawalpur in the Cholistan desert — Pakistan's largest solar park.

III. Transmission: why high voltage, and what the lines suffer

Transmission is where the most marks in this topic are won, and it all starts with one fact: electricity is transmitted at high voltage to reduce power loss in the lines. The loss in a conductor is I²R, so for a given power, raising the voltage lowers the current, and the loss falls with the square of the current. That is why a step-up transformer stands at every generating station, and why long-distance lines run at 400 kV and above. The line itself is a set of compromises. Its conductors are ACSR — Aluminium Conductor Steel Reinforced — aluminium for conductivity and lightness, steel for strength. A bundled conductor, several sub-conductors per phase, is used on high-voltage lines to reduce corona discharge and minimise power losses. Corona is the ionisation of the air around the conductor, which begins when the voltage passes the disruptive critical voltage; it wastes power, makes a hissing sound and produces ozone, and its loss grows as the conductor diameter falls. The skin effect is the other loss the papers love: in an AC conductor the current concentrates near the surface, so the centre of a thick conductor carries almost nothing — and direct current has no skin effect at all, which is one more reason HVDC is attractive for very long distances. The proximity effect is its neighbour: the current in one conductor is pushed aside by the magnetic field of a conductor close by. The Ferranti effect is the surprise of a long line: on no load, the receiving-end voltage rises above the sending-end voltage, because the line's capacitance charges through its inductance. A long line also sags between its towers, and the sag grows when the conductor heats and expands — which is why lines are strung tighter in winter than in summer. The surge impedance loading, SIL, is the natural loading of a line: SIL = V²/Z, so a 132 kV line with a surge impedance of 400 ohms carries about 43.56 MW at its surge impedance loading. High-voltage direct current, HVDC, is preferred for very long distances because it reduces transmission losses and improves efficiency, and Pakistan's HVDC line — the Matiari to Lahore line at ±660 kV — has a capacity of 4,000 MW. The line that feeds power on either side of the main transmission line is called secondary transmission.

Why high voltage
  • Loss in a conductor is I²R; raising the voltage lowers the current, so the loss falls with the square of the current.
  • A step-up transformer at the generating station raises the voltage for long-distance transmission.
  • Long-distance transmission uses 400 kV and above; Pakistan's main network runs at 500 kV.
Conductors and their troubles
  • ACSR — Aluminium Conductor Steel Reinforced: aluminium conducts, steel gives strength.
  • Bundled conductors — reduce corona discharge and minimise power losses.
  • Corona — ionisation of the air around the conductor; its loss increases as the conductor diameter decreases.
  • Skin effect — AC current flows mainly through the outer surface of the conductor; HVDC has no skin effect.
  • Proximity effect — a neighbouring conductor's magnetic field distorts the current distribution.
  • Ferranti effect — on no load, the receiving-end voltage is higher than the sending-end voltage.
  • Sag — grows as the conductor heats and expands; a line sags more in summer than in winter.
The numbers of a line
  • Surge impedance loading: SIL = V²/Z — 132 kV and 400 Ω gives 43.56 MW.
  • HVDC: Pakistan's Matiari–Lahore line, ±660 kV, 4,000 MW.
  • Generation is typically 11 kV; transmission is 500 kV on the main network.

IV. Distribution: substations, feeders and cables

Distribution is the quiet half of the system and the half the assistant-lineman papers test hardest, because it is the part a lineman touches. From the grid station, power goes out at 11 kV on feeders to the distribution substations, and a distribution transformer there lowers the voltage for supply to homes. A substation is the place where the voltage level is changed and the power is distributed, and its busbar is the common conductor that gathers the incoming power and hands it to the outgoing feeders. Three shapes of distribution network are asked, and the papers always ask which is which. A radial system has one path from the substation to each consumer: it is simple and cheap, it is the system commonly used for residential areas, and when its one path fails, everyone beyond the fault loses supply. A ring main system gives each consumer two paths: if one side of the ring fails, power comes the other way, so its advantage over the radial system is improved reliability and continuity of supply. An interconnected system goes further still, with several sources and paths feeding the same network. In towns, ring main units — RMUs — are preferred in urban networks because they provide multiple power supply paths in a small space. Underground, the cable matters: XLPE, cross-linked polyethylene, insulation is preferred over paper-insulated cables because XLPE has a higher thermal resistance, so the cable can run hotter and carry more. The wires themselves are sized by the American Wire Gauge, AWG: as the AWG number increases, the wire gets thinner, so a high current needs a thick conductor — a low AWG number. The two distribution voltages to carry in the head are 11 kV at the primary side and 400/230 V at the consumer's side.

Radial against ring against interconnected
  • Radial — one path to each consumer; simple and cheap; commonly used for residential areas; one fault cuts everyone beyond it.
  • Ring main — two paths to each consumer; improved reliability and continuity of supply; RMUs give multiple paths in urban networks.
  • Interconnected — several sources and paths; the most reliable and the most expensive.
The parts of distribution
  • Substation — changes the voltage level and distributes power to consumers.
  • Busbar — conducts and distributes power to the outgoing feeders.
  • Feeder — carries electricity from a substation to the consumers.
  • Distribution transformer — a step-down transformer that lowers the voltage for supply to homes.
  • XLPE cable — cross-linked polyethylene insulation, preferred underground for its higher thermal resistance.
  • AWG — American Wire Gauge; a larger AWG number means a thinner wire, so high currents need thick (low-AWG) conductors.

V. Transformers in the power system, and their protection

The transformer is the device that makes the whole voltage ladder possible: it increases or decreases the voltage level, stepping AC voltage up or down, and it is the one machine this page treats as part of the system rather than as a machine to be studied on its own. A step-up transformer at the power station raises the voltage for transmission, and a step-down transformer in distribution lowers it for homes. The core of a transformer is commonly silicon steel, which keeps the iron losses low. A transformer is protected twice over. The Buchholz relay guards it against internal faults: it is a gas-operated relay fitted in the pipe between the tank and the conservator, and gas given off by an internal fault collects in it and trips the alarm or the breaker. The differential relay guards it by comparison: it compares the current entering the transformer with the current leaving it, and any difference means a fault inside, so it trips. Both relays answer the same question — what is wrong inside the transformer — and the papers ask them both. The voltage a transformer delivers is not fixed: a tap changer varies the turns ratio, and so the output voltage, so the supply can be held steady as the load changes. A transformer is cooled by its oil, which both insulates and carries heat away; ONAN cooling — Oil Natural, Air Natural — is the natural circulation of the oil and the natural flow of air over the radiators, with no pumps and no fans. The rating of a transformer is written in kVA, because its loading is set by the current and the voltage, not by the power factor of the load.

The two transformer relays
  • Buchholz relay — gas-operated; protects the transformer against internal faults; gas from a fault collects in the relay and trips it.
  • Differential protection — compares the currents entering and leaving the transformer; a difference means an internal fault, so it trips.
  • Both protect the transformer itself; the distance relay protects the line.
Tap changer and cooling
  • Tap changer — varies the turns ratio to regulate the output voltage as the load changes.
  • Transformer oil — provides insulation and cooling.
  • ONAN — Oil Natural, Air Natural: oil circulates and air flows by natural convection, with no pumps or fans.
  • Transformer rating — expressed in kVA.

VI. Protection: relays, breakers, fuses and earthing

Protection is the system's immune system: it must find a fault, isolate it, and leave the healthy part of the system running. The order of the chain is fixed and the papers test it. A protective relay detects the fault; the circuit breaker interrupts the fault current and isolates the faulty section. The relay is the brain and the breaker is the muscle — a relay alone cannot break a current, and a breaker alone cannot decide when to break it. The main job of a circuit breaker is to interrupt current during a fault, and the main job of a protective relay is to detect the fault and trip the circuit breaker. There are several kinds of relay, and each answers a different question. A distance relay measures impedance: it operates when the impedance falls below a predetermined value, because a fault close by looks like a small impedance and a fault far away looks like a large one — so with a reach setting of 80% on a 250 km line it protects 200 km, and a measured impedance of 15 ohms against a 20-ohm setting means the fault is inside its zone and the relay operates. A directional relay is used for transmission-line protection to tell forward fault currents from reverse ones. A differential relay compares the currents at the two ends and trips on a difference. A busbar protection scheme protects the busbar by isolating the faulty section. Pilot wire protection compares the currents at both ends of a transmission line over a pilot wire. A numerical relay does all of this faster and more accurately than an electromechanical relay, and travelling-wave protection is the scheme used for evolving faults. The fuse is the simplest protector of all: it breaks the circuit when too much current flows, by melting when the current exceeds a safe value. A fuse wire is made of a material with high resistivity and a low melting temperature, and a fuse in a household circuit is connected in the live (phase) wire. A miniature circuit breaker, an MCB, does the same job but can be reset: it trips on overload and on short circuit, and it is switched back on instead of replaced. The isolator, or disconnector, is different from both: it has no arc-quenching device, so it must only be opened when the circuit is already dead — it isolates for maintenance, it never breaks a load current. The most frequent fault in a power system is the single line-to-ground fault, and the most severe is the three-phase fault. Earthing is the protection of people: the main purpose of earthing electrical equipment is to provide a safe path for fault current to earth, and the earth wire in a house carries fault current safely to the ground and protects people from electric shock — it is coloured green, or green and yellow. A residual-current device, an RCD, is used for shock safety: it trips when it senses current leaking to earth. A lightning arrester, or surge arrester, protects equipment from lightning strikes and surges by giving the surge a safe path to earth. The insulator holds the line and stops the current from passing into the tower: on a tall steel tower the line hangs from a glass or ceramic disc, a suspension (disc) insulator, and porcelain is the material commonly used for insulators on overhead lines. In a string of suspension insulators the voltage is not shared equally: the disc nearest the conductor carries the highest voltage, which is why the string efficiency is always less than 100%. Fault analysis itself uses symmetrical components, because they simplify the analysis of unbalanced faults.

The protection chain
  • Protective relay — detects the fault and trips the circuit breaker.
  • Circuit breaker — interrupts the fault current and isolates the faulty section.
  • Fuse — melts and breaks the circuit when the current is too high; fuse wire has high resistivity and a low melting temperature; connected in the live wire.
  • MCB — trips on overload and short circuit and can be reset; a fuse must be replaced.
  • Isolator (disconnector) — opens only on a dead circuit; it has no arc quenching and never breaks load current.
  • RCD — trips on leakage current to earth; used for shock safety.
The relays, one line each
  • Distance relay — operates when the measured impedance falls below its setting; 80% reach on a 250 km line protects 200 km.
  • Directional relay — tells forward fault currents from reverse ones.
  • Differential relay — compares currents at the two ends; a difference means an internal fault.
  • Busbar protection — isolates the faulty section of the busbar.
  • Pilot wire protection — compares the currents at both ends of a transmission line.
  • Numerical relay — faster and more accurate fault detection than an electromechanical relay.
  • Travelling-wave protection — used for evolving faults in a transmission system.
Faults and earthing
  • Most frequent fault — single line-to-ground fault. Most severe fault — three-phase fault.
  • Earthing — provides a safe path for fault current to earth; the earth wire is green, or green and yellow.
  • Lightning arrester (surge arrester) — protects equipment from lightning strikes and surges.
  • Insulator — holds the line and stops current passing into the tower; suspension (disc) insulator of porcelain; the disc nearest the conductor carries the highest voltage.
  • Symmetrical components — simplify the analysis of unbalanced faults.

VII. Load, load factor and tariffs: the money side

A power station is judged by its load, and the papers test the load with four ratios that sound alike and are not the same. Learn them as fractions, with the bigger number underneath. The load factor is the average load divided by the maximum demand: it says how steadily the station was used, and a high load factor means the plant was well used. The demand factor is the maximum demand divided by the connected load: it says how much of everything connected was ever on at once, and it is always less than one. The diversity factor is the sum of the individual maximum demands divided by the maximum demand of the whole system: because not everyone peaks at the same hour, it is always greater than one — if the separate peaks add to 600 kW but the system peak is 500 kW, the diversity factor is 1.2. The plant capacity factor is the average load divided by the plant's rated capacity: it says how much of what the plant could have made it actually made. The load curve is the picture behind all four: the area under the load curve is the energy consumed, and the base load is the steady minimum that must be supplied all day, while the peak load is the short, high demand on top of it. Base-load plants run continuously; peak-load plants are started only for the peak. The tariff is how the consumer pays for all of this. A two-part tariff has a fixed charge, based on the maximum demand, and a running charge, based on the units of energy used — the fixed charge pays for the plant that must exist, and the running charge pays for the fuel that is burned. The load-flow study is the calculation that holds the whole network together: it determines the voltage levels, the power flows and the losses in the network under steady-state conditions. It is solved, for large systems, by the Newton-Raphson method, because of its fast convergence, and it uses per-unit values, which normalise the system values so that voltages, currents and impedances on different sides of a transformer can be compared directly. In the study, the slack bus is the bus that takes up the transmission losses, so that the generation and the load balance. Power factor belongs here as a load problem, not as a circuit definition: an inductive industrial load has a lagging power factor, and it is improved by connecting capacitors in parallel, or by a synchronous condenser, or by a static VAR compensator, which gives dynamic voltage support and reactive power compensation. Series capacitors in a long line compensate its inductive reactance, and flexible AC transmission systems — FACTS — exist to enhance the controllability and stability of the grid. A phasor measurement unit, a PMU, measures voltage and current phasors in real time and so enhances grid stability. The smart grid ties all of this together: advanced metering infrastructure, AMI, gives real-time monitoring and two-way communication between the utility and the consumer, demand-side management handles real-time demand response and load balancing, and SCADA — Supervisory Control and Data Acquisition — supervises and controls the system from a control centre. Power line communication, PLC, is the communication technology commonly used for real-time data exchange in smart grids.

The four load ratios
  • Load factor — average load / maximum demand.
  • Demand factor — maximum demand / connected load; always less than 1.
  • Diversity factor — sum of individual maximum demands / maximum demand of the system; always greater than 1.
  • Plant capacity factor — average load / rated plant capacity.
Load curve and tariff
  • Area under the load curve — the energy consumed.
  • Base load — the steady minimum demand, supplied all day. Peak load — the short, high demand on top of it.
  • Two-part tariff — a fixed charge on maximum demand plus a running charge per unit of energy used.
Load flow and the smart grid
  • Load-flow study — voltage levels, power flows and losses under steady-state conditions; solved by the Newton-Raphson method.
  • Per-unit system — normalises system values for comparison across voltage levels.
  • Slack bus — accounts for the transmission losses.
  • AMI — real-time monitoring and two-way communication with consumers.
  • SCADA — Supervisory Control and Data Acquisition.
  • PMU — real-time measurement of voltage and current phasors; enhances grid stability.
  • Static VAR compensator — dynamic voltage support and reactive power compensation.

VIII. Pakistan's power sector: who runs what

Pakistan's power sector has a shape the papers ask about directly, and it is worth learning as a chain of names. WAPDA — the Water and Power Development Authority — was set up under the WAPDA Act of 1958 to develop the water and power resources of the country on a unified basis; it builds and operates the large hydroelectric stations, including Tarbela, Mangla, Warsak and Ghazi Barotha. The national transmission grid — the 500 kV and 220 kV network that carries power between the stations and the cities — is operated by NTDC, the National Transmission and Despatch Company. The power is then sold on to the distribution companies, the DISCOs, which supply the consumers in their areas: LESCO in Lahore, IESCO in Islamabad, FESCO in Faisalabad, GEPCO in Gujranwala, MEPCO in Multan, PESCO in Peshawar, HESCO and SEPCO in Sindh, QESCO in Quetta and TESCO in the tribal areas, with K-Electric supplying Karachi as a private utility. The sector is regulated by NEPRA, the National Electric Power Regulatory Authority, which sets the tariffs. The newest link in the chain is the HVDC line from Matiari to Lahore, at ±660 kV with a capacity of 4,000 MW, which carries power from the south to the load centres of Punjab. The generation mix is hydro from the dams, thermal from gas and coal, nuclear from Karachi and Chashma, and a growing share of solar and wind. When generation cannot meet demand, the result is the load shedding every candidate knows: a planned cut in supply when demand is greater than supply. The four facts to carry into the paper are the full form of WAPDA, the name of the grid operator, the largest hydroelectric station, and the first major hydroelectric project — Water and Power Development Authority, NTDC, Tarbela Dam, and Warsak Dam.

Who runs what
  • WAPDA — Water and Power Development Authority, set up under the WAPDA Act 1958; builds and operates the large hydroelectric stations.
  • NTDC — National Transmission and Despatch Company; operates the national transmission grid.
  • DISCOs — the distribution companies (LESCO, IESCO, FESCO, GEPCO, MEPCO, PESCO, HESCO, SEPCO, QESCO, TESCO); K-Electric supplies Karachi.
  • NEPRA — National Electric Power Regulatory Authority; regulates the sector and sets tariffs.
The landmarks
  • Largest hydroelectric power station — Tarbela Dam, 4,888 MW, on the Indus.
  • First major hydroelectric project — Warsak Dam, 243 MW, completed 1960, on the Kabul.
  • Largest earth-filled dam in the world — Tarbela Dam.
  • HVDC line — Matiari to Lahore, ±660 kV, 4,000 MW.

How to study this topic

Take the sections in order, because each one uses the words of the one before it: the system first, then generation, then transmission, then distribution, then transformers and protection, then load and tariffs, then Pakistan's sector. Inside each section, learn the reason before the single fact: high voltage exists because loss is I²R; a circuit breaker exists because a fault current must be stopped; earthing exists because a fault current must have a safe path. Then learn the numbers with their units — 11 kV generated, 500 kV transmitted, 132 kV at the grid station, 230 V at home, 50 Hz everywhere in Pakistan, 4,888 MW at Tarbela, 4,000 MW on the HVDC line. Keep a personal list of the pairs that sound alike: load factor against demand factor against diversity factor against capacity factor; radial against ring against interconnected; distance relay against differential relay against directional relay; fuse against MCB against isolator; Buchholz against differential; corona against skin effect against Ferranti effect; base load against peak load; WAPDA against NTDC against NEPRA. For every question you miss, read the explanation and say the rule aloud — especially the numerical ones, where the working is the learning: the hydro formula, the SIL, the distance relay's reach, the coal burned per hour. When you can answer every question on a section without looking, move on and come back after a day; that second visit is what moves a fact from short memory into long memory.

More facts to learn

  1. <p><b>In a power system, what is the main purpose of a transmission line?</b><br>To carry electrical power from a power station to the places where it is used.</p> <p><b>In a power system, what is the main purpose of a power station?</b><br>To generate electrical power</p> <p><b>In a power system, what is the main job of a generator?</b><br>To produce electricity</p> <p><b>In a power system, what is a load?</b><br>The equipment that uses electrical power.</p> <p><b>What is the frequency of the electricity supply in Pakistan?</b><br>50 Hz</p> <p><b>What is the standard frequency of electricity supply in the United States?</b><br>60 Hz</p> <p><b>In a hydroelectric power plant, what is the main factor that determines the power output?</b><br>The height of the water head and flow rate</p> <p><b>Which factor primarily determines the efficiency of a thermal power plant?</b><br>The temperature difference between the heat source and the sink</p> <p><b>In a thermal power plant, what is the primary energy conversion that takes place?</b><br>Heat → Mechanical → Electrical</p> <p><b>What is the primary purpose of an economizer in a thermal power plant?</b><br>To preheat the feedwater using residual heat from the flue gases</p> <p><b>A hydroelectric power station has a water flow rate of 500 cubic meters per second and an effective head of 120 meters
  2. If the overall efficiency of the plant is 85%, what is the approximate power output? (Take g = 9.81 m/s² and water density = 1000 kg/m³?</b><br>500 MW</p> <p><b>In a nuclear power plant, what is the primary function of a moderator?</b><br>To slow down fast neutrons and sustain the chain reaction</p> <p><b>Modern generators have the ability to generate approximately ______?</b><br>13kV - 30kV</p> <p><b>At what voltage is electricity typically generated in a power station?</b><br>11 kV.</p> <p><b>Why is electricity transmitted at high voltage?</b><br>To reduce power loss in the lines</p> <p><b>In a power system, what is the main job of a step-up transformer at a power station?</b><br>It raises the voltage for long-distance transmission</p> <p><b>What is the main purpose of an electrical substation?</b><br>To change voltage levels and distribute power.</p> <p><b>In a power system, what does a 'feeder' carry?</b><br>Electricity from a substation to the consumers.</p> <p><b>On a tall steel tower, the power line does not touch the metal directly; it hangs from a glass or ceramic disc
  3. What is the job of this disc, called an insulator?</b><br>To hold the line and stop the current from passing into the tower.</p> <p><b>Which material is commonly used as an insulator in overhead transmission lines?</b><br>Porcelain</p> <p><b>What type of insulator is used to support high-voltage transmission line conductors?</b><br>Suspension (disc) insulator.</p> <p><b>ACSR conductor stands for:</b><br>Aluminium Conductor Steel Reinforced</p> <p><b>Why is a bundled conductor configuration used in high-voltage transmission lines?</b><br>To reduce corona discharge and minimize power losses</p> <p><b>The skin effect in an AC transmission line causes the current to flow mainly through which part of the conductor?</b><br>The outer surface</p> <p><b>What is corona in a high-voltage transmission line?</b><br>The ionisation of air around the conductor.</p> <p><b>The corona loss in a transmission line increases with which of the following?</b><br>Decrease in conductor diameter</p> <p><b>What is the Ferranti effect?</b><br>Voltage rise at the receiving end on no load</p> <p><b>Why are high-voltage direct current (HVDC) transmission systems preferred for long-distance power transmission?</b><br>They reduce transmission losses and improve efficiency.</p> <p><b>A 100 km, 132 kV transmission line has a surge impedance of 400 Ω
  4. What is its surge impedance loading (SIL)?</b><br>43.56 MW</p> <p><b>Which voltage level is used for the main high-voltage transmission network in Pakistan?</b><br>500 kV.</p> <p><b>Which voltage level is typically used for long-distance power transmission?</b><br>400kv &amp; above</p> <p><b>A 3-phase, 4-wire system is used mainly to supply which kind of load?</b><br>Unbalanced loads with a neutral return</p> <p><b>The transmission line feeding power on either side of the main transmission line is called?</b><br>Secondary transmission</p> <p><b>Why are series capacitors used in long-distance AC transmission lines?</b><br>Improve power factor by compensating for inductive reactance</p> <p><b>What is the primary reason for using flexible AC transmission systems (FACTS) in modern power grids?</b><br>To enhance the controllability and stability</p> <p><b>Why are static VAR compensators (SVGs) used in power transmission systems?</b><br>To provide dynamic voltage support and reactive power compensation</p> <p><b>Which technology in a smart grid enhances grid stability by providing real-time measurement of voltage and current phase angles?</b><br>Phasor Measurement Unit (PMU)</p> <p><b>In a power system, what is the main job of a distribution transformer?</b><br>It lowers the voltage for supply to homes.</p> <p><b>In a power system, what is the main job of a transformer?</b><br>To increase or decrease the voltage level</p> <p><b>At what voltage is electricity supplied to homes in Pakistan?</b><br>230 V.</p> <p><b>What is the primary purpose of a step-down transformer in distribution systems?</b><br>Reduce voltage</p> <p><b>What is the primary function of a busbar in a substation?</b><br>To conduct and distribute power to outgoing feeders</p> <p><b>Which type of power distribution system is commonly used for residential areas?</b><br>Radial system</p> <p><b>What is the main advantage of using a ring main distribution system over a radial system?</b><br>Improved reliability and continuity of supply</p> <p><b>In a power distribution system, why are ring main units (RMUs) preferred in urban networks?</b><br>They provide multiple power supply paths</p> <p><b>In underground power distribution systems, why is XLPE (cross-linked polyethylene) insulation preferred over paper-insulated cables?</b><br>XLPE has a higher thermal resistance</p> <p><b>In electrical cables AWG stands for _______?</b><br>American Wire Gauge</p> <p><b>As the value of AWG increases the thickness of wire?</b><br>Decreases</p> <p><b>For high current flow in electrical circuits one needs _____?</b><br>Thick conductors</p> <p><b>Which material is commonly used for the core of a transformer?</b><br>Silicon steel</p> <p><b>Name the equipment protected by the Buchholz relay.</b><br>Transformers</p> <p><b>Which relay is used to protect a transformer against internal faults?</b><br>Buchholz relay</p> <p><b>A power transformer rated at 100 MVA, 220 kV/33 kV is protected by a differential relay
  5. If the CT ratios are 1000:5 on the HV side and 5000:5 on the LV side, what is the purpose of the relay?</b><br>To detect internal faults within the transformer</p> <p><b>Which protection scheme is commonly used for detecting faults in a transformer?</b><br>Differential protection</p> <p><b>What is the primary function of a protective relay in a power system?</b><br>Detect faults</p> <p><b>In a power system, what is the main job of a circuit breaker?</b><br>Interrupts current during a fault</p> <p><b>Which component is used to protect power distribution systems from overcurrent?</b><br>Circuit breaker</p> <p><b>In a power system, what does a fuse do?</b><br>It breaks the circuit when too much current flows.</p> <p><b>A common method of protection is to use a ______ in the lighting circuit.</b><br>Fuse</p> <p><b>The property of the wire used for fuse making?</b><br>High resistivity and low melting temperature</p>